In a triple phase system, metering from the neutral to a phase, how many volts should there be?

Study for the GFA Lighting and Electric Test. Enhance your skills with flashcards and multiple choice questions. Each question includes hints and explanations to get you ready for your exam!

Multiple Choice

In a triple phase system, metering from the neutral to a phase, how many volts should there be?

Explanation:
In a three-phase wye system with a neutral, the voltage from neutral to any one phase is the phase-to-neutral voltage. In the common 120/208 V arrangement, that phase voltage is 120 V, while the voltage between any two phases (line-to-line) is about 208 V because V_LL = √3 × V_LN (√3 × 120 ≈ 208). So metering from neutral to a single phase should read 120 V in this typical setup. (If the system were 277/480 V, neutral-to-phase would read 277 V instead.)

In a three-phase wye system with a neutral, the voltage from neutral to any one phase is the phase-to-neutral voltage. In the common 120/208 V arrangement, that phase voltage is 120 V, while the voltage between any two phases (line-to-line) is about 208 V because V_LL = √3 × V_LN (√3 × 120 ≈ 208). So metering from neutral to a single phase should read 120 V in this typical setup. (If the system were 277/480 V, neutral-to-phase would read 277 V instead.)